By far the most popular positive STRICTLY PLUMBING INFORMATION SHARING FORUM board on the Net. Ask any toilet, sink, faucet, pump, water quality and other plumbing related questions here. Plumbing professional and DIY tips, tricks, shortcuts, remodeling, plumbing advice forum and blog. Please refrain from asking business, pricing, legal or any other non strictly plumbing related questions and we also ask for only positive comments and no advertising. 

New TopicSearchLog In Newest Messages
 Kickboard Heater
Author: Anonymous User

OK one last question for tonight.
I am going to replace a bulky baseboard heating unit with a kickspace heater under the vanity. I've seen 2 types of installation instructions. 1] route the copper under the cabinet and cut out an access panel inside the cabinet for maintenance, or 2] connect with flexible tubing so the heating unit can be slid out the front for maintenance. Any preferences?

Reply To This Message

 Re: Kickboard Heater
Author: packy (MA)

there is no comparison between hard piped and flexable. i will not install a kickspace heater any other way but flexable. use the heatway rubber hose kit. it contains 8ft. of specially designed 1/2" ID hose, four 1/2" copper sweat to hose adapters and four self tite hose clamps. do a google search for heatway.
one word of caution, do not use automotive hose and compression type clamps. the heatway hose has an oxygen barrier in it while regular hose does not. be sure to leave enough electric wire to slide the heater out.

Reply To This Message

 Re: Kickboard Heater
Author: hj (AZ)

If it is replacing a section of standard baseboard heating, then it may be in a loop system, and reducing it to 1/2" through the kickboard heater will have a detrimental effect on the rest of that section's heat output.

Reply To This Message

 Re: Kickboard Heater
Author: Anonymous User

Right HJ, reducing a 3/4" loop from 40,000 btu's to about 15,000 less the toe kicks output.

Reply To This Message

 Re: Kickboard Heater
Author: packy (MA)

as noted below..
you have to install a kickspace heater with a monoflo tee and a regular tee. most commonly used would be a 3/4 copper x 1/2 copper variety.
simply put, you remove the baseboard heater and in the cellar you reconnect the loop with full size pipe. in this piece of pipe, you put 2 tees. one is a monoflow tee and the other is a regular tee. put short 1/2" copper nipples and ball valves. you can then refill and purge the loop and install the kickspace heater in a nice warm enviroment.
when i install ball valves for a kickspace heater, i like to use one valve with a drain button on the side with the button facing the heater. . when the install is done, open the valve without the button first and open the button on the other valve. this will purge the air thru the heater and out the button. run some water out the button for 30 seconds or so and close the button and open the closed valve.
voila.. heater is in, air is purged and no water on the floor upstairs.
(how's my french hj?)

Reply To This Message

 Re: Kickboard Heater
Author: Anonymous User

The current baseboard is already teed off the 3/4 loop (1/2" tee) and nothing else is in this tee. So I should be able to cut out the old baseboard and repipe the new, right? Great idea on the ball valve, I won't have to drain the system if the heater needs replacing. I will go with the heatway tubing kit. Thanks.
I bought a Beacon Morris Twin Flo heater. What is the maintenance schedule for this unit, how long will it last. Thanks.

Reply To This Message

 Re: Kickboard Heater
Author: hj (AZ)

In that case I would want to see exactly how the connection was made, at both ends of the baseboard, as to whether the kickspace heater will even work correctly.

Reply To This Message

 Re: Kickboard Heater
Author: Anonymous User

I see no difference between the two. Both have 1/2" copper in and through the heat exchanger and out back to the 3/4 loop. If water will flow thru the baseboard it will flow thru the kickspace. What are you worrying about? Thanks.

Reply To This Message

 Re: Kickboard Heater
Author: packy (MA)

there is no maintainance for that heater. the part that wears out first is the bearing assembly that the impellor spins on. 10-15 years for the bearing but they are replacable.
make sure to leave enough space around the heater for cold air to get to blower. just follow directions and you'll be fine.

Reply To This Message

 Re: Kickboard Heater
Author: Anonymous User

I found another answer to my question. See the thread subject : Kickspace Heater Stopped Working.
Gives a good explanation regarding hot water flow.
The safest install is using a monoflow tee as packy suggested.

Reply To This Message

 Re: Kickboard Heater
Author: hj (AZ)

I am not "worried" but you cannot just put a tee in a hot water system and expect the unit to heat properly. There has to be some "resistance" to flow between the two tees equal or greater than the resistance of the baseboard, or kickboard, heater or the hot water will go merrily on its way past the two tees rather than try to "fight" its way up the lines to the new heater. You do not have to take my word for this, and it will not bother me if you do not, but it is a fact that heating system designers have to cope with for EVERY component of a heating system. If yours works properly, then there is "someone" acting as a guardian angle and watching over even poorly designed systems. Mono Flo tees take care of this problem, but that is not what you say you have, and which is why I stated that I would like to see the system, namely to see if a MonoFlo tee might have been installed.



Post Edited

Reply To This Message

 Re: Kickboard Heater
Author: hj (AZ)

C'est si bon, monsieur. Mais, vous n'avez pas,..............Oops. Back to the United States. But you have not addressed how to get air out of the kickspace heater after the initial purge.

Reply To This Message

 Re: Kickboard Heater
Author: Anonymous User

Okay I got in the crawlspace and here are the details.
First bathroom :
The main loop is 1" copper.
The current baseboard is 3/4" copper, coming off the main loop with a monoflow tee on the supply side, standard tee on the return side. Distance between tees is about 30".
I want to remove the baseboard and install a 1/2" kickboard heater.

The second bathroom:
Has 1" iron loop (old part of the house) with iron monoflow tees on both supply and return sides. The current radiator is 3/4" copper. I want to remove the radiator and install 1/2" kickboard heater.

What are the recommended connections? I am wondering if I am putting in too much restriction into the system.

I have found a couple local contractors who say they will sell me some short pieces of Onix tubing so I want to run copper through the floor and Onix to the blower.

See the Subject "Replacing baseboard with fan heater" for updated info.



Post Edited

Reply To This Message


Note: Inappropriate messages or blatant advertising will be deleted. We cannot be held responsible for bad or inadequate advice.

Warning: Plbg.com has no control over external content that may be linked to from messages posted here. Please follow external links with caution.

Plbg.com is strictly for the exchange of plumbing related advice and NOT to ask about pricing/costs, nor where to find a product (try Google), nor how to operate or promote a business, nor for ethics (law) and the like questions.

Plbg.com is also not a place to ask radiant heating (try Heatinghelp.com), electrical or even general construction type questions. We are exclusively for plumbing questions.

Click here to view our old forum messages



to: Contact Us
to: Plumbing Manufacturers Address Directory
to: Plumbing Links Site
to: How to show an image
to: theplumber.com
to: Plbg Statistics
to: our FAQ's
to: Advisor List
to: Common Plumbing Terms
We're sponsored by:
The Leading Online Plumbing Supplier Since 1995
  We're sponsored by:
The Leading Online Plumbing Supplier Since 1995

Copyright© 2014 Plbg.com. All Rights Reserved.